出风口一直出风, 一会儿冷风, 一会儿热风。很不爽。这好象不正常吧。 以前好象不这样。锅炉的控制开关上的风扇设的是自动。请好心人帮助解答。
 
那是因为你的HRV一直开着.
如果不在乎那点电费,开着挺好的, 空气新鲜.

如果想省点电呢, 就把HRV关了,或者怎么重新设置一下.
 
:p 电费不菲。
 
家里24小时设定22度。但是冷风吹得很难受。HRV确实一直开着的。现在关了, 还是吹冷风。把furnace的控制开关(一楼的)关了,居然还在吹。我晕。
 
应该是风扇的控制开关出问题了,还是找人看看吧。如果自己handy的话也可以自己换。

HRV的风扇与炉子的风扇是两码事。
 
肯定是坏了,我们家的原来也这样,后来修好了,不过还是散着的
 
on hrv, there are two buttons, to set the hrv in a testing mode, which will keep the hrv running. turn off your furnace, and press that button, the hrv/furnace should stop.

i had the same issue when i first day get the new house, and tested out the furnace on/off button. it didn't work so I called harding (the company who installed furnaces for lots of builders in ottawa). they sent in a guy with in 30 minutes, found out the guy who tested my hrv didn't put the hrv in normal mode back.

把furnace的控制开关(一楼的)关了: you mean put the fan in off mode on your hemostat, not turning off the power of your furnace (in basement). if you turned off the power and furnace fan still blowing, you might find a new way to save energy cost for you home:)
 
if you moved in a new house, you are eligible to a free orientation meeting from the funace comapny. Call them and make an apointment.
 
if it is a new house, you may be eligible to a free orientation meeting from the furnace dealer. it will teach you how to control the HRV and the furnace.
 
谢谢各位的答复。其实大家都说到点子上了,可我当时不明白。今天来人看了。就是按一下在HRV上的一个button,灯不亮了,就好了。如果断电后再来电或者furnace的总电源(basement的)关了又开,都会导致HRV在一楼的开关不起作用, 进入Test mode。
 