安装中央吸尘器的问题

  • 主题发起人 主题发起人 QING
  • 开始时间 开始时间

QING

知名会员
注册
2004-12-19
消息
154
荣誉分数
1
声望点数
128
从Costco买的Hoover牌子的。自己安装时遇到一问题:说明书上说要20Amp的插座,我家地下室只有15Amp的插座,怎么办呢?谁有这方面的经验?谢谢。
 
I'd assume that you are to install the central vacuum in the unfinished part of the basement. Then you could run a 20A circuit from the electrical panel to the central vacuum spot.

You will need to install a 20A circuit break - Normally you have to run #12 wire with 20A breaker.
 
最初由 LiteUser 发布
I'd assume that you are to install the central vacuum in the unfinished part of the basement. Then you could run a 20A circuit from the electrical panel to the central vacuum spot.

You will need to install a 20A circuit break - Normally you have to run #12 wire with 20A breaker.
Thank you for your reply.
I do not know if it is easy to install the 20A breaker by myself. Do I have to hire someone to do that?
 
It's quite simple to add a circuit, but be extremely careful. Always turn off the main power when you work on circui breaker. I'd suggest you get a few books (quite a lot from the public library) and make youself familar with electrical stuff.

If you're not comfortable with that, you might want to find an electrician to do it, but I don't know how much it would cost.
 
最初由 LiteUser 发布
It's quite simple to add a circuit, but be extremely careful. Always turn off the main power when you work on circui breaker. I'd suggest you get a few books (quite a lot from the public library) and make youself familar with electrical stuff.

If you're not comfortable with that, you might want to find an electrician to do it, but I don't know how much it would cost.
Again thank you for your suggestion.
 
是的,换一个20安空气保险开关(20A breaker)
如果楼主不会的话,我可以帮你.
 