according to your schematic, please check the thermostat connected to the gas valve. If the temperature does not rise to a burning level, the gas valve will be shut off by itself. The thermostat does that as well. This is also a common failure.
Please take a close-up pic of the fan/limit switch and also the gas valve assy. Please also include the burner section so that I can tell you where the thermostat is.
我再看了一下电路图, 觉得好像不是Fan limit的问题, 因为 24v一直有,如果有问题, 变压器就会断电, 没有24v的输出, 现在有24v供电, 起码它能控制气体阀门打开一会, 点燃大火后再被Fan limit控制,切断110v供电,24v没有了,气体阀门关闭熄灭大火, 火苗Pilot不熄灭. 我也觉得是气体阀门控制器的可能性高些. 因为现在大火不能被点燃. 不知对否?
To iiwii:
1) yes, Pilot always lights and stable by itself.
2)No, Burner never fires after it had problem.
3) I set fan in auto position, but the fan is always on .
Thanks
谢谢楼上的答复!![]()
上个月我请人清洗了furnace, 然后开Furnace后忘记开送风电机约一小时, 后打开送风电机,furnace正常工作了2天, 然后就不工作了.
Furnace的后挡盖子原来是盖好的,为了拍照才打开. 火苗一直都有,另附上多图, 望有用.
电压测量: RH--W. 26V, RH--Y 26V, RH--G 26V 全是交流电压.RH=RC.
电路图里那个继电气体阀门控制器 都有26v的交流电.
电阻: 室内温度小于设定温度时. RH---W 之间导通, 反之 不通. Y--RH 电阻一直变.
请问, 那个FAN/LIMIT CONTROL 是如何工作的? 我认为温度调节器正常, 不知对否?